    I own a 2 story (separated) house. I rent out the lower apartment and live in the upper. Both have washer/dryer hook ups and both are used. The contractor who renovated the house when I moved in ran both dryer vents to a single Y connector and vented them outside. There is no outside access to the vent as it's under a porch. About 6 months ago, my tenant hooked up her dryer and I noticed, every time she'd turn it on, it would partially vent through MY dryer. This is obviously unacceptable. I had a handyman in today to run an outside vent to the rear of the house.

    Here's where it gets tricky. The lower 1/2 of the house is poured concrete finished in stone. The upper half is typical construction (all wood). I was planning on running the outside vent downstairs as it has a dropped ceiling thus easy access. Turns out nobody has anything that will drill a 4" hole through solid concrete and the only way to get to the little bit of wood above it (without going through my floor) is to cut a 4" hole through a floor joist. There's a pocket behind the joist that would allow the outside vent but I don't want anybody cutting 4" out of a 6" joist. Just doesn't seem like a good idea. My dryer is on an INSIDE wall so I can't vent it as most would.

    I wish I had taken pics but hopefully you get the idea. Does anybody have any suggestions? I can probably hire a carpenter to go through the joist and shore it up however it needs to be done but I can see some serious $$$ going that route. I can have another vent run through the front of the house but I don't even know how the original contractor did that as it's probably 4' from the wall to whatever he drilled through. In hindsight, that probably isn't even the best idea as I don't see any way to secure/seal the pipe.

    I'm hoping one of you knowledgable folks has some suggestions.

    HAGO!

  2. #2
    Active Member spyder01's Avatar
    Join Date
    May 2018
    Location
    millsboro,delaware
    Posts
    446
    Spyder Garage
    0

    Default

    I clean vents along with my powerwash business.If it was me I would call the guys at betterventing.com and ask them,if they dont know then search or post the question on their venting forum,good luck.
    :
    : 2017 RTL ORBITAL BLUE

  3. #3
    Very Active Member
    Join Date
    Feb 2020
    Location
    N. Wilkesboro, NC
    Posts
    1,902
    Spyder Garage
    0

    Default

    It appears their forum registration is closed.

  4. #4
    Active Member spyder01's Avatar
    Join Date
    May 2018
    Location
    millsboro,delaware
    Posts
    446
    Spyder Garage
    0

    Default

    Quote Originally Posted by MONK View Post
    It appears their forum registration is closed.
    Try calling tomorrow
    :
    : 2017 RTL ORBITAL BLUE

  5. #5
    Very Active Member ulflyer's Avatar
    Join Date
    Jun 2011
    Location
    Near Lexington, NC
    Posts
    2,218
    Spyder Garage
    0

    Default

    Could you have a metal plate made with a 4+ inch hole to screw onto the joist? That should be sufficient to shore up the joist. Or perhaps a 1" metal bar along the top and bottom?
    Two Wheelers from 1963-2011

    Three Wheelers:
    2011 RT(Red)
    2014 RT(white)
    2016 F3T(red)
    2022 RT current ride(silver)
    __________________
    2016 Slingshot
    2018 Vanderhall
    2019 Slingshot

  6. #6
    Ozzie Ozzie Ozzie Peter Aawen's Avatar
    Join Date
    Dec 2013
    Location
    Australia; Sth Aust, Adelaide Hills
    Posts
    9,643
    Spyder Garage
    0

    Default

    Any chance you could just lose the 'Y' connector & just run a new parallel vent pipe alongside the original from there on out??

    Or maybe you could put a 'wind & storm protector' type 'flap/non-return' valve in the outlet pipe on the back of each dryer (altho it might possibly still work if you put those valves anywhere in the outlet pipes running from the back of each dryer out as far as the 'Y'??) so that whenever the 'other' dryer is on & venting, the force of its output air closes off the 'other' dryer's flap valve, stopping any venting out thru that dryer. That should solve the 'wrong way' venting problem when only one dryer is on, still allow each dryer to operate as normal, and yet force any vented air to go out the right way whenever either or both dryers are operating....

    Dunno if any if that helps, but maybe... Good luck!
    2013 RT Ltd Pearl White

    Ryde More, Worry Less!

  7. #7
    Very Active Member wyliec's Avatar
    Join Date
    Dec 2008
    Location
    Syracuse, NY
    Posts
    7,321
    Spyder Garage
    0

    Default

    How about power exhaust after the Y, energized by either dryer.

    https://www.fantech.net/our-solution...dryer-exhaust/

  8. #8
    Very Active Member BLUEKNIGHT911's Avatar
    Join Date
    Aug 2011
    Location
    Central VERMONT
    Posts
    20,390
    Spyder Garage
    0

    Default

    A 4 inch hole can be a problem or not it depends on whether it has to bear a LOAD. If it is a joist with NO SUPPORT where you need to hole then you can't make a hole - period. Forget any type of support plates, it will be un-safe. ... However if this 2x6 is the vertical support over a SILL plate and the joists run from there out ( as floor supports ) then it not really load bearing and can be done ..... Good luck .... Mike

  9. #9
    Very Active Member wyliec's Avatar
    Join Date
    Dec 2008
    Location
    Syracuse, NY
    Posts
    7,321
    Spyder Garage
    0

    Default

    Quote Originally Posted by wyliec View Post
    How about power exhaust after the Y, energized by either dryer.

    https://www.fantech.net/our-solution...dryer-exhaust/
    Wiring may be able to be run thru the vent if running outside the vent poses a problem; high temp insulation wiring.

  10. #10
    Active Member Bluetrees's Avatar
    Join Date
    Aug 2020
    Location
    Connecticut
    Posts
    41
    Spyder Garage
    0

    Default

    Monk, Home Depot (and many others) sells an in-line 4" valve to prevent outside air coming in.

    How about placing it in-line just beyond your dryer but before the Y.
    When the other units dryer turns on the valve should prevent that air from coming your way.
    F3S
    Black, with black stuff on it.

  11. #11
    Active Member
    Join Date
    Oct 2020
    Location
    Southern, USA
    Posts
    81
    Spyder Garage
    0

    Default

    Peter hit the nail on the head earlier IMO.

    The product you are looking for is called a "backdraft damper" (4in)
    Install anywhere after one of the units but before the Y

    Simple and nothing to go wrong aside from needing a bit of extra lint cleaning.
    Edit: Behind the dryer for easy cleaning (Bluetrees basically said the same thing I am seeing now)
    71zno0oMc5L._AC_SL1500_.jpg

  12. #12
    Very Active Member bmccaffrey's Avatar
    Join Date
    Oct 2013
    Location
    rome new york
    Posts
    2,337
    Spyder Garage
    0

    Default

    Quote Originally Posted by oh400ex View Post
    Peter hit the nail on the head earlier IMO.

    The product you are looking for is called a "backdraft damper" (4in)
    Install anywhere after one of the units but before the Y

    Simple and nothing to go wrong aside from needing a bit of extra lint cleaning.
    Edit: Behind the dryer for easy cleaning
    71zno0oMc5L._AC_SL1500_.jpg
    This will work. Will let air out but not back in

  13. #13
    Very Active Member Lew L's Avatar
    Join Date
    Mar 2015
    Location
    forrest above Reno, Nv
    Posts
    3,632
    Spyder Garage
    1

    Default

    The backdraft damper will work. They are always in vent fans for bathrooms/ laundry rooms. Also ar 4" core drill will make it through solid concrete. I had to drill holes through the foundation stem wall when I added on the the house.

    Lew L
    Kaos----- Gone but not forgotten.

    2014 RTS in Circuit Yellow, farkle-ing addiction down to once every few months. ECU FLASH IS GREAT.
    2014 RTS , Circuit Yellow

  14. #14
    Very Active Member Gwolf's Avatar
    Join Date
    Apr 2019
    Location
    Florida Swamp
    Posts
    1,962
    Spyder Garage
    2

    Default

    There are ways to cut a 4 inch hole through solid concrete. None of the local contractors may not be able to do it, but it can be done. Seen it plenty of times putting pipes through 8 to 12 inch thick floors in chemical plants and manufacturing plants.
    2019 F3-S , Black & Silver

  15. #15
    Very Active Member Woodaddict's Avatar
    Join Date
    Mar 2017
    Location
    Salisbury,NC
    Posts
    802
    Spyder Garage
    2

    Default

    yes they do make 4" core concrete drills. any type of backdraft damper, your only asking for trouble with lint build up. should SEPARATE them. i don't think building codes would even allow this double venting.
    find the right plumber will have core drill. i will look over for you monday, i do alot of handyman work and just built my house with contractor, doing alot of the work
    2015 Spyder RT Ltd- bUrp - only add the "U", 2010 Honda NT700V-red,2010 Honda NT700V-silver retired @201,111 miles, 1997 Honda PC800, 1996 Honda PC800, Honda CT500, Honda Shadow 500, 1978 Suzuki GS550, 1973 Suzuki TC125, other assorted smaller bikes, Suzuki TM400



  16. #16
    Very Active Member
    Join Date
    Sep 2014
    Location
    USA
    Posts
    4,651
    Spyder Garage
    0

    Default

    As Lew stated a 4 inch core bit will work for drilling a 4 inch hole in concrete.

    Maybe able to rent one from Home Depot or someone local.

  17. #17
    Very Active Member Lew L's Avatar
    Join Date
    Mar 2015
    Location
    forrest above Reno, Nv
    Posts
    3,632
    Spyder Garage
    1

    Default

    And just to complicate matters:


    Every 90*bend in duct work is the same as 15 to 20 FEET of straight duct.
    The HVAC company the did my first dryer vent did not know this as they put 6 -90* elbows to cover a distance of 2.5 ' to an outside wall ( in the wall ,down,up and out). And yes it clogged up with lint. I rectified the situation with a short length of smooth duct and 1 elbow. Dryer works great.
    Good luck,
    Lew L
    Kaos----- Gone but not forgotten.

    2014 RTS in Circuit Yellow, farkle-ing addiction down to once every few months. ECU FLASH IS GREAT.
    2014 RTS , Circuit Yellow

  18. #18
    SpyderLovers Sponsor BajaRon's Avatar
    Join Date
    Aug 2007
    Location
    Greeneville, TN
    Posts
    13,590
    Spyder Garage
    0

    Default

    Quote Originally Posted by ulflyer View Post
    Could you have a metal plate made with a 4+ inch hole to screw onto the joist? That should be sufficient to shore up the joist. Or perhaps a 1" metal bar along the top and bottom?
    I agree. But there is an easier way. Get 3/8" plywood and make 2 pieces 3' long. Laminate them to both sides of the joist with construction adhesive and suck them up with some long wood screws. Unless there is a grand piano or some other very heavy object sitting right over this joist, This should give you more than enough reinforcement. I've done this myself. Much less work and cost than boring a 4" hole through solid concrete. I'd suspect there may be some rebar in there as well.
    Last edited by BajaRon; 11-16-2020 at 01:11 PM.
    Shop Ph: 423-609-7588 (M-F, 8-5, Eastern Time)

    Only SLOW people have to leave on time...





  19. #19
    Very Active Member Gwolf's Avatar
    Join Date
    Apr 2019
    Location
    Florida Swamp
    Posts
    1,962
    Spyder Garage
    2

    Default

    Quote Originally Posted by BajaRon View Post
    I agree. But there is an easier way. Get 3/8" plywood and make 2 pieces 3' long. Laminate them to both sides of the joist with construction adhesive and suck them up with some long wood screws. Unless there is a grand piano or some other very heavy object sitting right over this joist, This should give you more than enough reinforcement. I've done this myself. Much less work and cost than boring a 4" hole through solid concrete. I'd suspect there may be some rebar in there as well.
    The hole will go right through any rebar that might be in the concrete. You can see where the rebar was in the cylindrical plugs that come out of the holes. The better core tools have diamond cutting surfaces.

    2019 F3-S , Black & Silver

  20. #20
    Active Member spyder01's Avatar
    Join Date
    May 2018
    Location
    millsboro,delaware
    Posts
    446
    Spyder Garage
    0

    Default

    Quote Originally Posted by BajaRon View Post
    I agree. But there is an easier way. Get 3/8" plywood and make 2 pieces 3' long. Laminate them to both sides of the joist with construction adhesive and suck them up with some long wood screws. Unless there is a grand piano or some other very heavy object sitting right over this joist, This should give you more than enough reinforcement. I've done this myself. Much less work and cost than boring a 4" hole through solid concrete. I'd suspect there may be some rebar in there as well.
    thats called sistering in a joist.I had to do it when I sold my last house and there was termite damage,but you dont do it with 3/8 plywood,use the same size wood thats already there like 2x12 and make it as long as you can easily fit like maybe 3 or 4 feet.Oh and use bolts with washers and nut if you can.If you ever have a home inspector look at it you'll be good.
    :
    : 2017 RTL ORBITAL BLUE

  21. #21
    Very Active Member
    Join Date
    Mar 2011
    Location
    oregon
    Posts
    627
    Spyder Garage
    0

    Default

    Quote Originally Posted by MONK View Post
    About as off topic as it can get, eh?

    I own a 2 story (separated) house. I rent out the lower apartment and live in the upper. Both have washer/dryer hook ups and both are used. The contractor who renovated the house when I moved in ran both dryer vents to a single Y connector and vented them outside. There is no outside access to the vent as it's under a porch. About 6 months ago, my tenant hooked up her dryer and I noticed, every time she'd turn it on, it would partially vent through MY dryer. This is obviously unacceptable. I had a handyman in today to run an outside vent to the rear of the house.

    Here's where it gets tricky. The lower 1/2 of the house is poured concrete finished in stone. The upper half is typical construction (all wood). I was planning on running the outside vent downstairs as it has a dropped ceiling thus easy access. Turns out nobody has anything that will drill a 4" hole through solid concrete and the only way to get to the little bit of wood above it (without going through my floor) is to cut a 4" hole through a floor joist. There's a pocket behind the joist that would allow the outside vent but I don't want anybody cutting 4" out of a 6" joist. Just doesn't seem like a good idea. My dryer is on an INSIDE wall so I can't vent it as most would.

    I wish I had taken pics but hopefully you get the idea. Does anybody have any suggestions? I can probably hire a carpenter to go through the joist and shore it up however it needs to be done but I can see some serious $$$ going that route. I can have another vent run through the front of the house but I don't even know how the original contractor did that as it's probably 4' from the wall to whatever he drilled through. In hindsight, that probably isn't even the best idea as I don't see any way to secure/seal the pipe.

    I'm hoping one of you knowledgable folks has some suggestions.

    HAGO!
    they make a heat pump dryer now that condensates the moisture and you don't have to vent
    2 happy happy spyders

  22. #22
    Very Active Member IdahoMtnSpyder's Avatar
    Join Date
    Jan 2014
    Location
    Idaho
    Posts
    9,778
    Spyder Garage
    1

    Default

    Instead of going through the joist can you go parallel to the joist to the rim board and out?

    2014 Copper RTS

    Tri-Axis bars, CB, BajaRon sway bar & shock adjusters, SpyderPop's Bumpskid, NBV peg brackets, LED headlights and modulator, Wolo trumpet air horns, trailer hitch, custom trailer harness, high mount turn signals, Custom Dynamics brake light, LED turn signal lights on mirrors, LED strip light for a dash light, garage door opener, LED lights in frunk, trunk, and saddlebags, RAM mounts and cradles for tablet (for GPS) and phone (for music), and Smooth Spyder belt tensioner.
    2014 RTS , Copper! (officially Cognac)

  23. #23
    Very Active Member
    Join Date
    Feb 2020
    Location
    N. Wilkesboro, NC
    Posts
    1,902
    Spyder Garage
    0

    Default

    Quote Originally Posted by IdahoMtnSpyder View Post
    Instead of going through the joist can you go parallel to the joist to the rim board and out?
    Unfortunately, no. I'd end up with an add'l 50' run and I'd still probably end up in concrete.